CathyInBlue
Grandmaster
As long as you feed the xfer switch from the 30 A genny with the same cable as you would feed with the 50 A genny. The 50 A breaker in the xfer switch would not protect a 30 A conductor from the 30 A genny if the genny were to overload and begin supplying more than 30 A. In fact, the 50 A xfer switch won't protect the 30 A genny at all, but then, it wouldn't prevent a 50 A genny from eating itself either. The issue is in protecting the cabling therefrom. A >30 A load placed on the system would be passed merrily by the xfer switch, and attempt to be met by the genny, but if the conductors between the two are insufficient, they can overload, overheat, and cause a fire. Of course, that is, unless the genny eats itself first, thus reducing the power on the wires to zero regardless of wouldbe load.Here's a question for an Electrician: Can I feed my 12.5K watt/50 amp manual transfer switch with a 7.8K watt/30 amp genny?